Heat2000 > General Category > General Board > Pressure Relief Valve discharged..

Pressure Relief Valve discharged..
 Moderated by: Al Gregory  
 New Topic   Reply   Print 
AuthorPost
endeavor
Member
 

Joined: Wed Dec 31st, 1969
Location:  
Posts: 8
 Posted: Tue Feb 20th, 2007 11:12 pm
 Quote  Reply 
Water Heater Pressure Relief Valve discharged..

We have a relatively new 40 gal SuperStor indirect oil fired water heater - it's heated by a Burnham v74 oil fired boiler.
 
Last week going into the basement and was surprised to find 30 gal of water on the floor which had clear signs it was from the water heaters pressure relief valve - we estimate it happened a few days earlier.
 
Our questions are to find out from experienced technicians simply this - what do you find that the most common reasons for this happening?
 
some notes:
~The pressure relief valve is a standard Watts 150 psi 210 f rating
~The Honeywell Aquastat model L4080b is the thermostat on the water heater set at 130 degrees.
~The boiler Zone Valve is by Taco
 
Being technically minded we were simply curious to find out which item was the most likely to be the cause:
 
~1st on our list is the water heaters thermostat switch for whatever reason would of failed to switch off the 24 vac to the Zone Valve and so the boiler would have kept heating the water heaters water up till it reached the boilers max water temp which is about 180-210 degrees....?
~2nd is the Taco Zone Valve off the boiler servicing the water heater, maybe it jammed and failure to close its valve...?
~3rd .... water heater pressure relief valve all the sudden goes bad...  nah...?
~4th ...way off the mark but is an interesting tidbit, is that we live in the Northeast US and this happened at the very midpoint of last weeks NorthEaster storm when it was right overhead (which had a pretty low pressure)  ..although I doubt that the low pressure could in any way even if ever so slightly be a contributor of some sort? ..still it's interesting coincidence?
 
We being curious to know which of the 1, 2, or 3 event is more likely to have caused it, so over a period of a week we would control cycle numerous times the hot water heater watching everything involved carefully, but the zone valve works fine, the thermostat shuts off right when the water reaches 130 degrees, etc... We can't make it fail again.
 
Irregardless, we've bought brand new all three same identical replacement parts = thermostat, taco zone valve, watts pressure relief valve.. but again, our question is wondering from you the "everyday hands on repairmen" what do you find which most often is the cause for a water heater pressure relief valve to release with our similar setup?
 
Thank you,

Last edited on Tue Feb 20th, 2007 11:13 pm by endeavor

Al Gregory
Administrator


Joined: Wed Dec 31st, 1969
Location: Massachusetts USA
Posts: 134
 Posted: Wed Feb 21st, 2007 01:15 am
 Quote  Reply 
Do you have an expansion tank on the cold water supply to the heater? You may need one if you are on well water or have a check valve on your water meter from the town water supply

endeavor
Member
 

Joined: Wed Dec 31st, 1969
Location:  
Posts: 8
 Posted: Wed Feb 21st, 2007 03:42 am
 Quote  Reply 
heaterman wrote: Do you have an expansion tank on the cold water supply to the heater? You may need one if you are on well water or have a check valve on your water meter from the town water supply
There is only an expansion tank on the boiler run of course, but none on the water heater supply side no; however we have our own well, and fwiw that setup has all been culligan replaced 6 months ago actually and the welltrol tank settings they set 40/60 psi from on/off, and at that junction has a 90 psi relief valve on it too.  The water heater Watts relief valve is set 150 psi but of course must take into consideration the water is very hot water too.. Wondering about the supply side I did watch the welltrol psi meter and it does shut off at 60 psi and so thought that was okay.

Please explain your thoughts on the expansion tank reasoning as it sounds interesting.

Thank you

Al Gregory
Administrator


Joined: Wed Dec 31st, 1969
Location: Massachusetts USA
Posts: 134
 Posted: Tue Mar 6th, 2007 04:49 am
 Quote  Reply 
As the water heater heats it builds presure and backs against the cold water supply side. You should have an expansion tank that is rated for domestic water installed